ISPE生物制药厂房设施定义:Controlled Not Classified (CNC): areas where HVAC systems are specifically designed to reduce airborne contaminants below the level of the ambient environment and both temperature and Relative Humidity (RH) are controlled more tightly than in the ambient environment. Claims for environmental control in these areas are related to the design of the system and installation qualification is common. No claim is made or qualified for the specific control of particulate. Typical systems will have heating, cooling and filtration meeting MERV 13 or better. These areas are sometimes referred to as “pharmaceutical” or “clean” areas within pharmaceutical facilities.
ISPE 空调系统指南:The US "CNC" has no equivalent to EU Grade D although the term Controlled Not Classified (CNC) has been used in the pharmaceutical industry and is discussed
in the ISPE Baseline® Guides for Sterile and Biopharmaceuticals (Reference 13, Appendix 12). A CNC space may meet ISO 8 at rest without the use of
HEPA filters if the airborne challenge is low. For further information on air filters, see Chapter 3 of this Guide. Therefore, a “CNC with monitoring” space could
look and perform similarly to a European Grade D space. |
|