B.6.2.3 Concentration of upstream aerosol challenge and its verification
The concentration of the aerosol challenge upstream of the filter should be between 10 mg/m3 and 100 mg/m3. Concentrations lower than 20 mg/m3 can reduce the sensitivity for leak detection. Concentrations greater than 80 mg/m3 can give rise to excessive filter fouling over an extended test period[18].
Appropriate measures should be taken for the verification of the homogenous mixing of the added aerosol to the supply airflow. The first time a system is tested it should be determined that sufficient aerosol mixing is taking place. For such validation all injection and sampling points should be defined and recorded.(这个大家都有做吗???)
The upstream aerosol concentration measurements taken immediately upstream of the filters should not vary more than ± 15 % in time about the average measured value. Concentrations lower than the average will reduce the sensitivity of the test to small leaks, while higher concentrations increase the sensitivity to small leaks. Further details as to how to conduct the air-aerosol mixing test should be agreed upon between customer and supplier. ASME N510-1989[1] and IEST-RP-CC034.2:1999 [18] may also be of value.


选自:http://www.atitest.com/knowledge-center/faqs/faq003-upstream-challenge-aerosol-introduction-point/
Upstream Challenge Aerosol Introduction Point
To ensure adequate upstream aerosol challenge mixing, it is strongly recommended to introduce the test aerosol at least ten duct diameters upstream of the filter(s) under test(至少在过滤器前10倍管道直径的地方引入检测气溶胶). If 10 duct diameters is not feasible, or adequate mixing is not obtained, sparge pipes, upstream baffles, turning vanes or a Stairmand disc, located four to six duct diameters upstream, will achieve adequate mixing(这些各位实际的使用中有接触过嘛???).
A Stairmand disk is a plate with the same geometric shape as the duct section blocking the center of the duct area. Air flowing past the disk creates vortices on the leeward side that compel turbulent and thorough mixing of the introduced aerosol and the dilution air stream. The required diameter of the Stairmand disk may be calculated using the following information.
Stairmand disk diameter equals the pipe (or duct) diameter divided by the square root of two (1.414213). Eg. a 12 inch duct would require a Stairmand disk 8.5 inches in diameter.
- See more at: http://www.atitest.com/knowledge ... thash.TNJW9H0j.dpuf

回复

使用道具 举报

药士
 楼主| 发表于 2017-1-15 21:13:46 | 显示全部楼层
求这两份文件资料 ASME N510-1989[1] and IEST-RP-CC034.2:1999 ,非常感谢啊!!!
回复

使用道具 举报

药士
发表于 2017-1-15 22:01:49 | 显示全部楼层
回复

使用道具 举报

药生
发表于 2017-1-16 16:07:41 | 显示全部楼层
回复

使用道具 举报

您需要登录后才可以回帖 登录 | 立即注册

本版积分规则

×发帖声明
1、本站为技术交流论坛,发帖的内容具有互动属性。您在本站发布的内容:
①在无人回复的情况下,可以通过自助删帖功能随时删除(自助删帖功能关闭期间,可以联系管理员微信:8542508 处理。)
②在有人回复和讨论的情况下,主题帖和回复内容已构成一个不可分割的整体,您将不能直接删除该帖。
2、禁止发布任何涉政、涉黄赌毒及其他违反国家相关法律、法规、及本站版规的内容,详情请参阅《蒲公英论坛总版规》。
3、您在本站发表、转载的任何作品仅代表您个人观点,不代表本站观点。不要盗用有版权要求的作品,转贴请注明来源,否则文责自负。
4、请认真阅读上述条款,您发帖即代表接受上述条款。

QQ|手机版|蒲公英|ouryao|蒲公英 ( 京ICP备14042168号-1 )  增值电信业务经营许可证编号:京B2-20243455  互联网药品信息服务资格证书编号:(京)-非经营性-2024-0033

GMT+8, 2024-11-25 03:55

Powered by Discuz! X3.4运维单位:苏州豚鼠科技有限公司

Copyright © 2001-2020, Tencent Cloud.

声明:蒲公英网站所涉及的原创文章、文字内容、视频图片及首发资料,版权归作者及蒲公英网站所有,转载要在显著位置标明来源“蒲公英”;禁止任何形式的商业用途。违反上述声明的,本站及作者将追究法律责任。
快速回复 返回顶部 返回列表